Hi Chris,
I am trying to convert from Enclosured based name to native device name, but it fails with this message:
vxdmpadm listenclosure EMC0
ENCLR_NAME ENCLR_TYPE ENCLR_SNO STATUS ARRAY_TYPE
============================================================================
EMC0 EMC 890090 CONNECTED A/A
vxdmpadm setattr enclosure EMC0 tpdmode=native
VxVM vxdmpadm ERROR V-5-1-11117 This operation is not allowed under enclosure based naming scheme
12-25-2008 12:14 AM
Hello,
You can change your namingscheme to osn first & then try the same command..
# vxddladm set namingscheme=osn
Going back to actual question of vxfentsthdw failure...
Couple of questions:
1. Do you see emcpower1a device from both the nodes ?
2. Have you verified that emcpower1a is same device on both the nodes ? you can verify this with serial number of the Lun.
3. Are you able to do normal SCSI enquiries on emcpower devices ?
# /etc/vx/diag.d/vxdmpinq /dev/vx/dmp/emcpower1a
I would think that powerpath should know how to sent down IO's down the paths & since you are able to see power devices in vxdisk list that means veritas DMP understands too that powerpath is underlying. SF 4.1 had built in support of TPD devices, I would assume that to work normally...