08-12-2013 08:08 AM
Hi,
We've upgraded quiet afew 5220's to 2.5.3 in the last week and have noticed an issue with the BBU status. All upgrades completed fine and appliances have been re-started several times, backup are working, however when running Monitor>Hardware Adapter we have an issue with the Intel RS2PI008 RAID controller cards (Can't pull the information directly from the appliance as its a secure site)
Adapter Model Adapter Status BBU Learn Charge Charging Status Volt Temp Manufacturing Date State Acknowledge
cycle active
Intel Raid OK No 60% NONE OK OK May 16, 2011 FAILED NO
Controller
RS2PI008
The RS2PI008 controller is only in afew of the bigger appliances, as this is for an additional shelf. The other RAID controller card SROMBSASMP2 is fine. All of the RAID write policies are set to WriteBack and the status is OK for each.
Has anyone else got this issue? Not sure if it is an actual issue, but the BBU status and charge level hasn't changed since the upgrade to 2.5.3 which is now over 72 hours ago.
Any help much appreciated
Solved! Go to Solution.
09-11-2013 06:55 AM
The BBU status check has been enhanced in 2.5.3 - it is in the release notes:
From the new features section:
The battery backup (BBU) monitoring logic has been enhanced to alert you
and Symantec AutoSupport of when it is time to replace the battery. Previously,
the logic monitored the relative charge of BBU. With this enhancement, the
logic monitors the absolute charge of the BBU to more accurately predict the
life of the battery. In addition, the monitoring logic detects when the absolute
charge drops to 65% or less. That is the point at which performance may
degrade. To avoid this situation, the BBU monitoring sends an alert to you and
Symantec AutoSupport when the absolute charge reaches 67%. That early
notification provides you with enough time to replace the BBU before
performance is affected.
08-13-2013 01:08 AM
Possibly best to get a Support call logged ASAP....
08-13-2013 02:45 AM
Yep got a support call logged so will see what they say.
08-21-2013 04:51 PM
Hi DMF-UK,
I hope you have got it resolved by now. I'm wondering if you end up replacing the BBU?
09-11-2013 05:52 AM
**Update**
Replaced the BBU which has resolved the issue. Strange how only 2.5.3 was reporting the issue and not 2.5.2.
09-11-2013 06:55 AM
The BBU status check has been enhanced in 2.5.3 - it is in the release notes:
From the new features section:
The battery backup (BBU) monitoring logic has been enhanced to alert you
and Symantec AutoSupport of when it is time to replace the battery. Previously,
the logic monitored the relative charge of BBU. With this enhancement, the
logic monitors the absolute charge of the BBU to more accurately predict the
life of the battery. In addition, the monitoring logic detects when the absolute
charge drops to 65% or less. That is the point at which performance may
degrade. To avoid this situation, the BBU monitoring sends an alert to you and
Symantec AutoSupport when the absolute charge reaches 67%. That early
notification provides you with enough time to replace the BBU before
performance is affected.